What minimum effective intensity must a visible appliance have in a sleeping area when the lens is less than 24 in. below the ceiling?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1072
- D: 177 cd
Explanation
In sleeping areas, a visible appliance within 24 in. of the ceiling must be at least 177 cd, because a smoke layer may obscure it. If it is 24 in. or more below the ceiling, 110 cd is sufficient. It must also be within 16 ft of the pillow.