A ceiling mounted strobe is to cover a square room on a 10 ft ceiling. Why can't the wall mounted candela table be used for it?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1074
- C: Ceiling units use their own table tied to ceiling height
Explanation
Ceiling mounted visible appliances use a separate table that relates room size and ceiling height to the required candela, because the light distribution differs from a wall mounted unit.