Which of these methods is NOT an acceptable way to check smoke detector sensitivity?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2003
- C: Spraying aerosol into the detector and watching for the LED
Explanation
A functional test with aerosol only confirms that smoke enters and causes alarm. It does not measure sensitivity. Acceptable methods are calibrated test methods, listed control equipment that reports sensitivity, or other approved calibrated means.