Question 2033 of 344 · NICET Fire Alarm Systems Level II
Why are notification appliances on a supervised NAC polarized (diode blocked)?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2033
- A: So supervision current flows only through the EOL
Explanation
The diode blocks reverse polarity supervision current through the appliances. Only the EOL carries it, so an open anywhere on the circuit is detected. In alarm, forward polarity powers the appliances.
More questions: Maintenance
- 2034Using Ohm's law, a circuit draws 0.5 A at 24 V. What is the circuit resistance?
- 2035A 24 VDC fire alarm relay coil has a resistance of 1200 ohms. What current does it draw?
- 2036A 24 VDC panel power supply delivers 3 A to its load. How much power is that?
- 2037Two 4.7 kilohm resistors are accidentally connected in parallel at the end of an IDC. What resistance does the panel see?
- 2038A technician measures 18.2 V at the last strobe on a NAC while the panel output reads 24.0 V in alarm. What is the voltage drop on the circuit?
- 2039Strobes on the end of a NAC flash dimly and some do not flash at all during the alarm test, while the first strobes work. What is the most likely cause?