A technician measures 18.2 V at the last strobe on a NAC while the panel output reads 24.0 V in alarm. What is the voltage drop on the circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2038
- D: 5.8 V
Explanation
Voltage drop = source voltage minus voltage at the far end = 24.0 V - 18.2 V = 5.8 V. If the appliances are listed for a minimum of 16 V, they still operate, but the margin under battery power must also be checked.