A technician finds that an addressable smoke detector reports a different device type than programmed. What type of trouble will the panel show?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2040
- D: A device type mismatch trouble
Explanation
Addressable panels compare the reported device type to the programmed type. A mismatch, such as a heat detector at an address programmed for smoke, produces a trouble so the error can be corrected.