Question 2042 of 344 · NICET Fire Alarm Systems Level II
What does a trouble signal indicate in a fire alarm system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2042
- C: A fault that could prevent proper operation
Explanation
Trouble signals report faults such as opens, grounds, power loss, or failed components. Supervisory signals report off normal conditions of other fire protection systems, such as closed valves.
More questions: Maintenance
- 2043Which of these conditions should produce a supervisory signal rather than a trouble signal?
- 2044A trouble signal must be annunciated within what time after the fault occurs?
- 2045When a trouble signal is silenced at the panel and the fault is not repaired, what happens?
- 2046What must the technician do when a system impairment is found during a service visit?
- 2047Which actions are part of a planned impairment procedure under NFPA 72?
- 2048After repairing a deficiency, what testing must be done?