Question 2050 of 344 · NICET Fire Alarm Systems Level II
A software change affects 3 devices. The system has 380 initiating devices total. How many unaffected devices must also be tested?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2050
- C: 38 devices
Explanation
377 devices are not directly affected. 10 percent of 377 is 37.7, rounded up to 38, which is below the 50 device cap. Together with the 3 affected devices and their functions, that is the minimum test scope.
More questions: Maintenance
- 2051A site specific software change is made on a system with 1200 initiating devices. What is the maximum number of unaffected devices required to be tested?
- 2052When the control unit firmware (executive software) is changed, what must be done?
- 2053How long must records of inspection, testing, and maintenance be retained?
- 2054How long must the original acceptance test records be retained?
- 2055Where must a copy of the site specific software be kept?
- 2057How must the documentation cabinet be labeled?