A site specific software change is made on a system with 1200 initiating devices. What is the maximum number of unaffected devices required to be tested?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2051
- C: 50 devices
Explanation
10 percent of about 1200 would be about 120, but the requirement caps the sample of unaffected devices at 50.