Question 3071 of 344 · NICET Fire Alarm Systems Level II
When should fire alarm shop drawings normally be approved by the AHJ?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3071
- B: Before installation work starts
Explanation
Most AHJs require plan approval before a permit is issued and installation begins. Working from approved drawings avoids costly rework found during inspection.
More questions: Submittal Preparation and System Layout
- 3072A heat detector listed for 25 ft spacing is installed on an 11 ft smooth ceiling. The multiplier for that height is 0.91. What is the adjusted spacing?
- 3073A heat detector listed for 50 ft spacing is planned for a 30 ft ceiling. The multiplier is 0.34. What spacing applies?
- 3074A 20 ft wide room uses spot smoke detectors with S = 30 ft. Every point must be within 21 ft of a detector. With one row down the center, what is the maximum spacing along the row?
- 3075A speaker set on its 1 W tap produces 84 dBA at 10 ft. What level is expected at 10 ft on the 2 W tap?
- 3076An SLC is limited by the manufacturer to 40 ohms of total loop resistance. Using 18 AWG solid (7.77 ohms per 1000 ft), what is the maximum one way distance for a Class B run to the farthest device?
- 3077Within what time must the battery charger be able to recharge fully discharged secondary batteries?