An SLC is limited by the manufacturer to 40 ohms of total loop resistance. Using 18 AWG solid (7.77 ohms per 1000 ft), what is the maximum one way distance for a Class B run to the farthest device?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3076
- D: About 2,570 ft
Explanation
Total conductor length allowed = 40 / 7.77 x 1000 = 5,148 ft. That is out and back, so the one way distance is about 2,574 ft. Larger wire allows a longer run.