Question 2010 of 297 · NICET Fire Alarm Systems Level III
Which test frequency does NFPA 72 assign to mechanical (vane) and pressure-type waterflow alarm devices?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2010
- C: Semiannually
Explanation
Waterflow alarm-initiating devices are tested semiannually, which is coordinated with the NFPA 25 sprinkler system test so water is flowed through the inspector's test connection. The test confirms the signal arrives within the allowed time.