A dirty smoke detector that has not been cleaned in years goes into alarm with no fire. How does NFPA 72 classify this?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2022
- D: Nuisance alarm
Explanation
An unwanted alarm caused by mechanical failure, malfunction, improper installation, or lack of proper maintenance is a nuisance alarm. Classifying unwanted alarms correctly helps the owner and AHJ focus on the right fix, here maintenance.