Question 2021 of 297 · NICET Fire Alarm Systems Level III
A student pulls a manual fire alarm box as a prank. How does NFPA 72 classify this alarm?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2021
- A: Malicious alarm
Explanation
NFPA 72 classifies unwanted alarms as malicious (a person acting with malice), nuisance (caused by malfunction, improper installation or lack of maintenance), unintentional (a person acting without malice) and unknown (cause not determined). A prank pull is malicious.
More questions: Maintenance
- 2022A dirty smoke detector that has not been cleaned in years goes into alarm with no fire. How does NFPA 72 classify this?
- 2023A maintenance worker sets off a detector with welding smoke while working without a hot work permit. How is this unwanted alarm classified?
- 2024Under NFPA 72, what does a semiannual test frequency mean in terms of allowed scheduling window?
- 2025A technician performed the previous annual test in March. Using the NFPA 72 definition of annual, which next test date still complies?
- 2026How long must inspection, testing, and maintenance records be retained under NFPA 72?
- 2027Which information must an inspection and testing report contain to be useful under NFPA 72?