Which information must an inspection and testing report contain to be useful under NFPA 72?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2027
- D: Date, technician, items tested, results, and deficiencies
Explanation
NFPA 72 provides a form for inspection and testing that captures the property, the service organization and technician, the devices and functions tested with results, and deficiencies and corrective actions. Reports without results cannot show compliance.
More questions: Maintenance
- 2028Before the annual test of a building, you are asked to write a test plan. What is its main purpose under NFPA 72?
- 2029The building has a clean agent suppression system released by the fire alarm system. What must be done before testing detectors in the protected room?
- 2030Where testing personnel leave a system with an uncorrected deficiency at the end of a visit, what should the Level III service manager require?
- 2031During the annual inspection you notice that a large open office has been divided into small offices with full-height walls since the last test. What should you do?
- 2032How must single- and multiple-station smoke alarms in dwelling units be handled with respect to age?
- 2033A carbon monoxide detector connected to the fire alarm system indicates an end-of-life signal. What is the correct response?