Question 2024 of 297 · NICET Fire Alarm Systems Level III
Under NFPA 72, what does a semiannual test frequency mean in terms of allowed scheduling window?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2024
- C: Twice per year, at intervals of at least 4 and no more than 8 months
Explanation
NFPA 72 defines frequencies with windows: annual is 9 to 15 months and semiannual is 4 to 8 months. The windows let service schedules flex without missing a required test.