Where testing personnel leave a system with an uncorrected deficiency at the end of a visit, what should the Level III service manager require?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2030
- D: Written notice to the owner describing the deficiency and the impairment status
Explanation
Deficiencies that are not fixed during the visit must be reported to the owner in writing so the owner can act and arrange interim measures where needed. NFPA 72 sets a short time frame for this notice when the condition is an impairment.
More questions: Maintenance
- 2031During the annual inspection you notice that a large open office has been divided into small offices with full-height walls since the last test. What should you do?
- 2032How must single- and multiple-station smoke alarms in dwelling units be handled with respect to age?
- 2033A carbon monoxide detector connected to the fire alarm system indicates an end-of-life signal. What is the correct response?
- 2034An engine-driven generator serves as part of the fire alarm system's secondary power. Which standard governs its testing?
- 2035An intermittent ground fault trouble comes and goes on a system with eight circuits. What is an efficient troubleshooting strategy?
- 2036A notification appliance circuit is in trouble. With the field wiring disconnected from the panel, you measure the resistance across the two field conductors and read an open circuit instead of the end-of-line resistor value. What does this indicate?