Question 2029 of 297 · NICET Fire Alarm Systems Level III
The building has a clean agent suppression system released by the fire alarm system. What must be done before testing detectors in the protected room?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2029
- C: Disable or isolate the releasing outputs, coordinating with the suppression contractor
Explanation
Testing initiating devices in a releasing system without isolating the release circuits can discharge agent, which is costly and can be hazardous. The test plan must identify releasing outputs and how they are disabled and restored.
More questions: Maintenance
- 2030Where testing personnel leave a system with an uncorrected deficiency at the end of a visit, what should the Level III service manager require?
- 2031During the annual inspection you notice that a large open office has been divided into small offices with full-height walls since the last test. What should you do?
- 2032How must single- and multiple-station smoke alarms in dwelling units be handled with respect to age?
- 2033A carbon monoxide detector connected to the fire alarm system indicates an end-of-life signal. What is the correct response?
- 2034An engine-driven generator serves as part of the fire alarm system's secondary power. Which standard governs its testing?
- 2035An intermittent ground fault trouble comes and goes on a system with eight circuits. What is an efficient troubleshooting strategy?