Question 2032 of 297 · NICET Fire Alarm Systems Level III
How must single- and multiple-station smoke alarms in dwelling units be handled with respect to age?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2032
- A: Replace them no more than 10 years after the date of manufacture
Explanation
NFPA 72 requires smoke alarms to be replaced not more than 10 years from the date of manufacture, or sooner if the manufacturer says so or they fail to respond to testing. System smoke detectors connected to a control unit are handled by sensitivity testing instead.
More questions: Maintenance
- 2033A carbon monoxide detector connected to the fire alarm system indicates an end-of-life signal. What is the correct response?
- 2034An engine-driven generator serves as part of the fire alarm system's secondary power. Which standard governs its testing?
- 2035An intermittent ground fault trouble comes and goes on a system with eight circuits. What is an efficient troubleshooting strategy?
- 2036A notification appliance circuit is in trouble. With the field wiring disconnected from the panel, you measure the resistance across the two field conductors and read an open circuit instead of the end-of-line resistor value. What does this indicate?
- 2037A short on a signaling line circuit drops out 120 devices on a large floor. Which design feature limits how many devices are lost to one short?
- 2038During the annual inspection of a 24 VDC system, you measure 27.3 V across the battery terminals with the charger connected. What does this reading usually indicate?