Question 2039 of 297 · NICET Fire Alarm Systems Level III
During the annual test of a duct smoke detector, which check is needed besides the functional alarm test?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2039
- C: Confirm it samples the airstream, such as by a pressure differential check
Explanation
A duct detector only works if air flows through its housing. Annual testing includes verifying that the sampling arrangement works, typically by measuring the pressure differential across the sampling tubes against the manufacturer's range, as well as the functional test.
More questions: Maintenance
- 2040During annual testing of an air-sampling smoke detection system, what transport time requirement applies to the farthest sampling port?
- 2041An addressable smoke detector reports a maintenance alert because its drift compensation has reached its limit. What is the correct response?
- 2042Which personnel does NFPA 72 recognize as qualified to perform inspection, testing, and maintenance of fire alarm systems?
- 2043Before the annual visit at a central station monitored building, what should the technician confirm with the central station operator?
- 2044Annual testing reveals that a beam smoke detector alarms at the correct attenuation filter, but its alignment is off and it reports trouble every few days. What is the right action?
- 2045Which description fits a central station service under NFPA 72?