During the annual inspection you find that a painter has painted several smoke detectors along with the ceiling. What should you do?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2059
- D: Treat them as deficient; clean or replace per the manufacturer
Explanation
NFPA 72 does not allow detectors to be painted, because paint can block smoke entry openings and change response. Painted detectors must be cleaned per the manufacturer or replaced, then tested.