A technician leaves the panel in walk test mode at the end of the day. Why is this a serious problem?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2058
- A: Normal alarm and output operation is usually suspended, so the system is impaired
Explanation
During walk test, alarms are usually not processed normally, outputs may be disabled, and signals may not be transmitted. Leaving the panel in that mode is an unplanned impairment, so the test plan must include restoration and a final check of system status.