A technician leaves the panel in walk test mode at the end of the day. Why is this a serious problem?

Exactly one answer is correct.

Show solution

Correct answer to question 2058

  • A: Normal alarm and output operation is usually suspended, so the system is impaired

Explanation

During walk test, alarms are usually not processed normally, outputs may be disabled, and signals may not be transmitted. Leaving the panel in that mode is an unplanned impairment, so the test plan must include restoration and a final check of system status.