Months after a renovation, your technician finds plastic dust covers still on several smoke detectors. How should this be handled?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2060
- B: Remove the covers, test the detectors, and document the corrected impairment
Explanation
Dust covers are for protection during construction only. A covered detector cannot sense smoke, so the area has been unprotected; remove the covers, clean or replace and test the detectors, and document the impairment and its correction.