Question 2078 of 297 · NICET Fire Alarm Systems Level III
Which test result best indicates a failing secondary power supply that needs immediate action?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2078
- C: Under alarm load, its voltage falls below the panel minimum
Explanation
The key performance requirement is that the secondary supply carries the system for the required standby time and then the alarm load. A battery whose voltage collapses under alarm load cannot meet that requirement and must be replaced.
More questions: Maintenance
- 2079A remote annunciator is dark during the annual inspection, but the main panel works normally. Which is the most likely category of problem to check first?
- 2080A system has repeated nuisance alarms from duct detectors when air handlers start. What is the most likely cause to investigate?
- 2081During the annual test, door holders on a corridor release correctly when the fire alarm activates, but one door does not fully close. Whose deficiency is it and what do you do?
- 2082Which statement about the presignal feature is correct?
- 2083The owner wants to stop the annual test of the elevator recall because it disrupts tenants. What should you advise?
- 2084During the annual inspection the record documentation cabinet is empty and the owner cannot find the drawings. What should the Level III recommend?