Question 2081 of 297 · NICET Fire Alarm Systems Level III

During the annual test, door holders on a corridor release correctly when the fire alarm activates, but one door does not fully close. Whose deficiency is it and what do you do?

Exactly one answer is correct.

Show solution

Correct answer to question 2081

  • C: Report it to the owner as a door closer deficiency

Explanation

The fire alarm function (release) worked; the door's failure to close is a door hardware issue covered by NFPA 80 and NFPA 101. The ITM report should note it so the owner can correct it, since the door is part of the smoke barrier.

Next to question ›