Question 2081 of 297 · NICET Fire Alarm Systems Level III
During the annual test, door holders on a corridor release correctly when the fire alarm activates, but one door does not fully close. Whose deficiency is it and what do you do?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2081
- C: Report it to the owner as a door closer deficiency
Explanation
The fire alarm function (release) worked; the door's failure to close is a door hardware issue covered by NFPA 80 and NFPA 101. The ITM report should note it so the owner can correct it, since the door is part of the smoke barrier.