Question 2077 of 297 · NICET Fire Alarm Systems Level III
The owner asks whether a smoke detector that tested within its listed range can be left in service despite being 14 years old. What does NFPA 72 base the decision on?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2077
- A: Test results and the manufacturer's instructions, not age alone
Explanation
For system smoke detectors, NFPA 72 relies on sensitivity and functional testing and the manufacturer's instructions. The 10-year replacement rule applies to smoke alarms, not to system detectors, although many manufacturers recommend replacement after about 10 years.