Per NFPA 72 Table 18.5.5.4.1(a), which effective intensity is required for a single wall-mounted strobe in a 30 ft by 30 ft room?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3021
- B: 30 cd
Explanation
The room spacing table for wall-mounted appliances lists 15 cd for 20 x 20 ft, 30 cd for 30 x 30 ft, 60 cd for 40 x 40 ft, and 95 cd for 50 x 50 ft, for one appliance per room.
More questions: Submittal Preparation and System Layout
- 3022A conference room is 38 ft by 40 ft. Using one wall-mounted strobe per the room spacing table, which minimum rating would you pick?
- 3023In a corridor 10 ft wide and 180 ft long, how must visible appliances be spaced?
- 3024The average ambient sound level in a factory is 85 dBA. What is the minimum average alarm level required for public mode audible signaling?
- 3025A private mode alarm is designed for a control room with 60 dBA average ambient. What minimum level is required?
- 3026What audible level is required at the pillow in sleeping areas, at a minimum?
- 3027What is the maximum sound pressure level allowed for audible notification appliances?