A conference room is 38 ft by 40 ft. Using one wall-mounted strobe per the room spacing table, which minimum rating would you pick?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3022
- C: 60 cd
Explanation
Room sizes are rounded up to the next table entry. A 40 x 40 ft room requires 60 cd with one wall appliance, and this room fits within that size.
More questions: Submittal Preparation and System Layout
- 3023In a corridor 10 ft wide and 180 ft long, how must visible appliances be spaced?
- 3024The average ambient sound level in a factory is 85 dBA. What is the minimum average alarm level required for public mode audible signaling?
- 3025A private mode alarm is designed for a control room with 60 dBA average ambient. What minimum level is required?
- 3026What audible level is required at the pillow in sleeping areas, at a minimum?
- 3027What is the maximum sound pressure level allowed for audible notification appliances?
- 3028In a voice evacuation system, which metric is commonly used to verify that messages are intelligible?