NICET Fire Alarm Systems Level III, Submittal Preparation and System Layout: all 75 questions
All questions from the Submittal Preparation and System Layout section for NICET Fire Alarm Systems Level III, each with the correct answer.
- 3001A panel draws 0.45 A in standby and 2.10 A in alarm. The system needs 24 hours of standby followed by 5 minutes of alarm, and you apply the 1.25 aging correction factor of NFPA 72 (2022/2025). What is the minimum battery capacity?
- 3002A system draws 0.30 A in standby and 1.80 A in alarm. With 24 hours standby, 5 minutes alarm, and no margin, what is the required battery capacity?
- 3003An in-building emergency voice/alarm communications system draws 0.80 A standby and 6.0 A in alarm. What alarm duration must the battery calculation use after the 24-hour standby?
- 3004In a battery calculation, which current values should be used for each device?
- 3005A 24 VDC notification circuit has 10 strobes drawing a total of 1.5 A. The farthest strobe is 300 ft from the panel on 14 AWG solid wire with 3.07 ohms per 1,000 ft. What is the approximate voltage drop at the end?
- 3006A strobe circuit is designed to start at a worst-case panel source voltage of 20.4 V. The strobes are listed for 16 to 33 V. What is the maximum allowable voltage drop on the circuit?
- 3007A 12 AWG stranded circuit has a resistance of 1.98 ohms per 1,000 ft. The load is 2.0 A at the end of a 250 ft run. What is the voltage drop?
- 3008A NAC calculation shows a 5.2 V drop, but only 3.5 V is allowed. Which change will reduce the drop the most?
- 3009What is the listed spacing of spot-type heat detectors in a room with a smooth ceiling 9 ft high, if the detector is listed for 50 ft?
- 3010A heat detector listed for 50 ft spacing is installed on a smooth ceiling 15 ft high. The ceiling height multiplier for over 14 up to 16 ft is 0.77. What is the adjusted spacing?
- 3011A heat detector listed for 30 ft spacing is installed on a smooth ceiling 21 ft high. The multiplier for over 20 up to 22 ft is 0.58. What is the adjusted spacing?
- 3012Under the 0.7 rule, how far may a spot-type detector with a nominal 30 ft spacing be from any point on the ceiling?
- 3013On a smooth ceiling, spot smoke detectors at a 30 ft spacing are installed. What is the maximum distance from a detector to a side wall?
- 3014A room is 60 ft by 90 ft with a smooth flat ceiling. Using spot smoke detectors at a 30 ft square spacing, how many detectors are needed?
- 3015A smooth ceiling has solid joists 10 in deep spaced 3 ft on center. How does this affect spot heat detector spacing?
- 3016A ceiling has beams 12 in deep spaced 6 ft on center. How is spot heat detector spacing adjusted?
- 3017A warehouse ceiling has beams 24 in deep and 10 ft on center. How should heat detection be laid out?
- 3018A sloped ceiling rises 2 ft over a horizontal run of 10 ft. Is it a sloping ceiling under NFPA 72 detector placement rules?
- 3019For a peaked ceiling, where must the first row of spot detectors be located?
- 3020When laying out detectors on a sloped ceiling, which dimension is used for spacing beyond the first row?
- 3021Per NFPA 72 Table 18.5.5.4.1(a), which effective intensity is required for a single wall-mounted strobe in a 30 ft by 30 ft room?
- 3022A conference room is 38 ft by 40 ft. Using one wall-mounted strobe per the room spacing table, which minimum rating would you pick?
- 3023In a corridor 10 ft wide and 180 ft long, how must visible appliances be spaced?
- 3024The average ambient sound level in a factory is 85 dBA. What is the minimum average alarm level required for public mode audible signaling?
- 3025A private mode alarm is designed for a control room with 60 dBA average ambient. What minimum level is required?
- 3026What audible level is required at the pillow in sleeping areas, at a minimum?
- 3027What is the maximum sound pressure level allowed for audible notification appliances?
- 3028In a voice evacuation system, which metric is commonly used to verify that messages are intelligible?
- 3029A large atrium with hard surfaces will have speakers. What design approach best supports intelligibility?
- 3030Which item must shop drawings include under NFPA 72?
- 3031Which document describes what each initiating device causes the system to do, such as recall elevators or release doors?
- 3032What does a riser diagram show on fire alarm shop drawings?
- 3033A plan reviewer rejects your shop drawings because product data sheets are missing for several devices. Why does this matter?
- 3034Under the IBC, a manual fire alarm system is required in a Group B occupancy when which condition is met?
- 3035Under the IBC, when is a manual fire alarm system required in a Group E occupancy?
- 3036Under the IBC, a manual fire alarm system is required in a Group A occupancy when which threshold is met?
- 3037Under the IBC, a Group A occupancy with 1,000 or more occupants requires which type of notification?
- 3038Under the IBC, which condition triggers a fire alarm system in a Group R-2 apartment building?
- 3039Under the IBC, when does a Group M occupancy require a manual fire alarm system?
- 3040Under the IBC, when is a manual fire alarm system required in a Group F occupancy?
- 3041Under NFPA 101, when is a fire alarm system required in a new business occupancy?
- 3042Under the IBC and IMC, smoke detectors in return air ducts of an HVAC unit are generally required above which airflow?
- 3043A plans reviewer asks for proof that two-wire smoke detectors will work with your selected control unit. What should you submit?
- 3044A speaker circuit has 22 speakers tapped at 1 W and 8 speakers tapped at 2 W. The design rule leaves 20 percent spare amplifier capacity. What minimum amplifier rating is needed?
- 3045A 24 V power supply has a 6 A output. Strobes on four circuits draw 1.4 A, 1.6 A, 1.2 A, and 1.5 A in alarm. Is the supply adequate?
- 3046Why must strobe current values be taken at the lowest operating voltage when sizing circuits?
- 3047Where more than two visible appliances are in the field of view, what must the design provide?
- 3048A strobe is mounted on the ceiling of a 30 ft by 30 ft room with a 10 ft ceiling. Which table should be used to select its rating?
- 3049In sleeping rooms, what is the minimum visible appliance rating when the appliance is more than 24 in below the ceiling?
- 3050What is the maximum distance allowed between the pillow and the visible appliance in a sleeping room?
- 3051Which document must the designer prepare before a mass notification system is designed?
- 3052A shop drawing shows the pathway class for each circuit. Why is this information important for review?
- 3053A designer must document where pathway survivability Level 2 or 3 is required. Which system type most often triggers this?
- 3054Which item is required in the documentation for a system using a performance-based detection design?
- 3055What is the main purpose of the record drawings (as-built drawings) for a fire alarm system?
- 3056An engineer of record returns your shop drawings marked 'Revise and Resubmit'. What should you do?
- 3057During review, you find that the architect's reflected ceiling plan has changed, moving lights to where you placed smoke detectors. What should the Level III do?
- 3058A large open office has ceiling-mounted supply diffusers. How far must spot smoke detectors be from them?
- 3059Which ceiling height condition generally points toward projected beam or air sampling detection rather than spot smoke detectors?
- 3060What does stratification mean for smoke detector design?
- 3061A projected beam smoke detector is being laid out. Which source governs the beam spacing and the distance to the ceiling?
- 3062Which information must the designer show for an air sampling smoke detection system?
- 3063Smoke detectors are used to release doors held open in a smoke barrier. Where are they typically located?
- 3064When a building has a smoke control system, what must fire alarm documents coordinate with?
- 3065Where must the location of the elevator recall initiating devices be shown?
- 3066Which document should a designer reference to find the elevator recall requirements on the elevator side?
- 3067A sprinklered Group B building has 600 occupants. Under the IBC, which feature can allow omitting most manual fire alarm boxes?
- 3068In a fully sprinklered building where most manual boxes were omitted under the IBC exception, how many manual boxes are still required?
- 3069Under the IBC, which occupancy group requires an automatic smoke detection system in corridors in most cases, such as nursing homes?
- 3070Under the IBC, which occupancy requires smoke alarms in sleeping units, even where a fire alarm system is installed?
- 3071In a high-rise building, which notification system does the IBC require?
- 3072Under NFPA 101, which occupancy generally requires a fire alarm system for any new building regardless of size?
- 3073A plan reviewer notes that the building's code is NFPA 101 and the IBC, and the two disagree on a threshold. How should the designer proceed?
- 3074Why should the design documents state the adopted code editions?
- 3075A plan review comment asks you to show the location of the fire alarm control unit and annunciator. What usually governs where they go?