Question 3023 of 297 · NICET Fire Alarm Systems Level III
In a corridor 10 ft wide and 180 ft long, how must visible appliances be spaced?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3023
- D: Within 15 ft of each end and no more than 100 ft apart
Explanation
For corridors up to 20 ft wide, 15 cd appliances may be used, located within 15 ft of each end and not more than 100 ft apart. A 180 ft corridor therefore needs at least three appliances.
More questions: Submittal Preparation and System Layout
- 3024The average ambient sound level in a factory is 85 dBA. What is the minimum average alarm level required for public mode audible signaling?
- 3025A private mode alarm is designed for a control room with 60 dBA average ambient. What minimum level is required?
- 3026What audible level is required at the pillow in sleeping areas, at a minimum?
- 3027What is the maximum sound pressure level allowed for audible notification appliances?
- 3028In a voice evacuation system, which metric is commonly used to verify that messages are intelligible?
- 3029A large atrium with hard surfaces will have speakers. What design approach best supports intelligibility?