Question 3029 of 297 · NICET Fire Alarm Systems Level III
A large atrium with hard surfaces will have speakers. What design approach best supports intelligibility?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3029
- B: More speakers at lower taps, nearer to listeners
Explanation
Highly reverberant spaces degrade speech. Distributing more speakers closer to listeners at moderate power increases direct sound relative to reflected sound, which improves intelligibility.