Under the IBC, when is a manual fire alarm system required in a Group E occupancy?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3035
- B: Occupant load of 50 or more, with exceptions
Explanation
IBC 907.2.3 requires a manual fire alarm system in Group E with an occupant load of 50 or more. Exceptions exist for small and fully sprinklered buildings under certain conditions.