Question 3034 of 297 · NICET Fire Alarm Systems Level III
Under the IBC, a manual fire alarm system is required in a Group B occupancy when which condition is met?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3034
- A: 500 or more occupants, or more than 100 above or below exit discharge
Explanation
IBC 907.2.2 requires a manual fire alarm system in Group B where the combined occupant load is 500 or more, or more than 100 persons above or below the lowest level of exit discharge, or for ambulatory care facilities. Sprinklers can allow omitting manual boxes under conditions.
More questions: Submittal Preparation and System Layout
- 3035Under the IBC, when is a manual fire alarm system required in a Group E occupancy?
- 3036Under the IBC, a manual fire alarm system is required in a Group A occupancy when which threshold is met?
- 3037Under the IBC, a Group A occupancy with 1,000 or more occupants requires which type of notification?
- 3038Under the IBC, which condition triggers a fire alarm system in a Group R-2 apartment building?
- 3039Under the IBC, when does a Group M occupancy require a manual fire alarm system?
- 3040Under the IBC, when is a manual fire alarm system required in a Group F occupancy?