Under the IBC, a manual fire alarm system is required in a Group B occupancy when which condition is met?

Exactly one answer is correct.

Show solution

Correct answer to question 3034

  • A: 500 or more occupants, or more than 100 above or below exit discharge

Explanation

IBC 907.2.2 requires a manual fire alarm system in Group B where the combined occupant load is 500 or more, or more than 100 persons above or below the lowest level of exit discharge, or for ambulatory care facilities. Sprinklers can allow omitting manual boxes under conditions.