A designer must document where pathway survivability Level 2 or 3 is required. Which system type most often triggers this?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3053
- D: Voice systems using partial evacuation or relocation
Explanation
Survivability rules mainly apply to voice systems that use relocation or partial evacuation, so that circuits serving areas not yet affected by fire keep working while occupants stay in place. The design must show the levels and the methods used.