Question 3059 of 297 · NICET Fire Alarm Systems Level III

Which ceiling height condition generally points toward projected beam or air sampling detection rather than spot smoke detectors?

Exactly one answer is correct.

Show solution

Correct answer to question 3059

  • A: Very high ceilings, such as atria

Explanation

Spot detectors are hard to reach and slow to respond at very high ceilings because smoke can stratify. Beam and air sampling detectors are often used, with design based on the manufacturer's listing and stratification analysis.

Next to question ›