Question 3059 of 297 · NICET Fire Alarm Systems Level III
Which ceiling height condition generally points toward projected beam or air sampling detection rather than spot smoke detectors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3059
- A: Very high ceilings, such as atria
Explanation
Spot detectors are hard to reach and slow to respond at very high ceilings because smoke can stratify. Beam and air sampling detectors are often used, with design based on the manufacturer's listing and stratification analysis.