When a building has a smoke control system, what must fire alarm documents coordinate with?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3064
- A: The smoke control sequence and zones
Explanation
Fire alarm inputs typically start smoke control sequences. The fire alarm design must match the smoke control zones and sequence so that the correct fans and dampers operate, and the interface must be shown and tested.
More questions: Submittal Preparation and System Layout
- 3065Where must the location of the elevator recall initiating devices be shown?
- 3066Which document should a designer reference to find the elevator recall requirements on the elevator side?
- 3067A sprinklered Group B building has 600 occupants. Under the IBC, which feature can allow omitting most manual fire alarm boxes?
- 3068In a fully sprinklered building where most manual boxes were omitted under the IBC exception, how many manual boxes are still required?
- 3069Under the IBC, which occupancy group requires an automatic smoke detection system in corridors in most cases, such as nursing homes?
- 3070Under the IBC, which occupancy requires smoke alarms in sleeping units, even where a fire alarm system is installed?