A projected beam smoke detector is being laid out. Which source governs the beam spacing and the distance to the ceiling?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3061
- B: The manufacturer's instructions and listing
Explanation
NFPA 72 states that beam detectors are installed per their listing and the manufacturer's instructions, with additional guidance in the annex. Spacing is often similar to spot detectors but always follows the listing.