A sprinklered Group B building has 600 occupants. Under the IBC, which feature can allow omitting most manual fire alarm boxes?

Exactly one answer is correct.

Show solution

Correct answer to question 3067

  • D: Sprinkler waterflow activating occupant notification

Explanation

IBC 907.2.2 includes an exception: manual boxes are not required where the building is fully sprinklered and the notification appliances activate on sprinkler waterflow. At least one manual box is still needed at an approved location.