A sprinklered Group B building has 600 occupants. Under the IBC, which feature can allow omitting most manual fire alarm boxes?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3067
- D: Sprinkler waterflow activating occupant notification
Explanation
IBC 907.2.2 includes an exception: manual boxes are not required where the building is fully sprinklered and the notification appliances activate on sprinkler waterflow. At least one manual box is still needed at an approved location.