Question 4040 of 297 · NICET Fire Alarm Systems Level III
A manufacturer releases a firmware update for the control unit after installation. How should the project manager handle it?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4040
- D: Evaluate it, and if installed, do reacceptance tests
Explanation
Changes to executive or site-specific software require reacceptance testing of affected functions and a percentage of other devices. Updates should be planned, documented, and tested.
More questions: Management and Supervision
- 4041A worker is exposed to noise of 95 dBA during testing of horns. What should the supervisor ensure?
- 4042A project has 4,800 labor hours estimated for installation. After 60 percent of the work is complete, 3,300 hours have been used. If the trend continues, about how many total hours will the job take?
- 4043A fire alarm job has a contract value of $240,000. Direct costs are $180,000 and allocated overhead is $36,000. What is the net profit as a percentage of the contract value?
- 4044The owner's representative asks your technician on site to add four strobes in a new room. What should the Level III project manager require before the work proceeds?
- 4045A subcontract requires the fire alarm contractor to carry insurance naming the general contractor as additional insured. What should the project manager provide before starting work?
- 4001Under OSHA construction rules, at what height must workers on a walking-working surface with an unprotected edge generally be protected from falls?