A building owner asks why the fire alarm ITM contract must also cover the interface relays for door release and fan shutdown. What is the best explanation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1046
- C: Emergency control function interfaces are part of the fire alarm ITM scope
Explanation
NFPA 72 Table 14.4.3.2 includes emergency control function interface equipment, verifying that the fire alarm output operates the interface. The controlled equipment itself may be tested by others, but the fire alarm side is within the fire alarm ITM scope.
More questions: Installation, Planning and Maintenance Management
- 1047When a building has several interconnected fire protection systems and is a high-rise, how often does the IFC require integrated testing in accordance with NFPA 4?
- 1048A department manager wants to cut costs by allowing an uncertified helper to perform the annual testing of a hospital system alone. Which NFPA 72 principle does this conflict with?
- 1049A new owner of a partly renovated building cannot find documentation for the existing system. Which step should a senior technician take first when evaluating it for a repair or replace decision?
- 1050On a large commissioning project, what is the main role of the commissioning authority (CxA)?
- 1051Under NFPA 4, who prepares the integrated system test plan that describes how interconnected fire protection and life safety systems will be tested together?
- 1052In what order do the phases of a typical fire protection commissioning process occur?