NICET Fire Alarm Systems Level IV, Installation, Planning and Maintenance Management: all 99 questions
All questions from the Installation, Planning and Maintenance Management section for NICET Fire Alarm Systems Level IV, each with the correct answer.
- 1001A hospital addition ties a new fire alarm network node into the existing campus system, smoke control, elevator recall and door release. Which document governs the testing that proves these interconnected systems work together as intended?
- 1002On a commissioning project, which document is written by the design team to explain how the owner's project requirements will be met, including code basis, assumptions and system descriptions?
- 1003Under the commissioning process described in NFPA 3, who normally develops the owner's project requirements (OPR)?
- 1004Six addressable smoke detectors are added to an existing loop, and the program is edited to map them to an existing elevator recall output. What reacceptance testing is required?
- 1005After a change to site-specific software, NFPA 72 requires testing of all functions known to be affected by the change. What additional sample of initiating devices not directly affected must also be tested?
- 1006Under NFPA 72, who is responsible for the inspection, testing and maintenance of a fire alarm system and its interconnected emergency control functions?
- 1007You are setting up an ITM program for a 40 story office tower. How often must sensitivity of the spot-type smoke detectors be checked after the first year test, assuming each result stays within the listed range?
- 1008In the ITM schedule you are building, how often must waterflow alarm devices and valve supervisory switches be functionally tested?
- 1009A facility has nonrestorable fixed temperature spot heat detectors installed 15 years ago. What does NFPA 72 require for these detectors?
- 1010Before starting the annual test of a monitored system in a hotel, which step does NFPA 72 require regarding signal recipients?
- 1011A data center fire alarm system interfaces with a preaction releasing panel, HVAC shutdown and door unlocking. What must be in place before the periodic test begins?
- 1012Under the International Fire Code, a required fire alarm system is out of service. What must happen?
- 1014A fire alarm contractor agrees to install a high-rise voice system for a fixed total price regardless of the actual cost. Which contract type is this, and who carries the risk of cost overruns?
- 1015An owner wants to pay the contractor's actual costs plus a fee, but with a ceiling the price cannot exceed. Which contract arrangement fits?
- 1016A campus retrofit is priced at a fixed amount per installed device because the final device count is not known at bid time. Which contract type is this?
- 1017The general contractor withholds 10 percent of each progress payment from the fire alarm subcontractor until the project is accepted. What is this withheld money called?
- 1018A contract states that the contractor will owe the owner 1,500 dollars for each calendar day the fire alarm acceptance test is late. What is this provision called?
- 1019Which bond protects the owner if the fire alarm contractor fails to complete the work according to the contract?
- 1020A supplier of fire alarm devices has not been paid by the electrical contractor. Which bond on a public project protects that supplier?
- 1021In a critical path schedule for a high-rise fire alarm installation, what characterizes the critical path?
- 1022An activity in your project schedule has an early start of day 12 and a late start of day 19. How much total float does it have?
- 1023Your estimated direct cost for a voice evacuation retrofit is 84,000 dollars. Company policy requires a 30 percent gross margin on the selling price. What selling price meets that policy?
- 1024A sales estimator applies a 25 percent markup to a job cost of 60,000 dollars. What gross margin results on the selling price?
- 1025A takeoff shows 480 addressable devices, each estimated at 0.75 labor hours including wiring terminations. With a crew of 3 technicians working 8 hour days, about how many working days will device installation take?
- 1026Last year your fire alarm company had 450,000 dollars of indirect overhead and 1,800,000 dollars of direct labor cost. If overhead is applied as a percentage of direct labor, what rate should the estimators use?
- 1027A service department has annual fixed costs of 360,000 dollars and earns a contribution margin of 40 percent on each dollar of revenue. What annual revenue is needed to break even?
- 1028Your service department must perform 1,600 annual inspections averaging 6 labor hours each. Each technician delivers about 1,400 billable hours per year. How many technicians are needed for this inspection workload alone?
- 1029On a percentage of completion job, you have billed 60 percent of the contract value while costs incurred represent 48 percent of the estimated total cost. How is the job reported on the work in progress schedule?
- 1030The owner asks your field crew to add 14 speakers in a new conference wing that is not in the contract scope. What should the project manager do before the crew starts the extra work?
- 1031A supplier who furnished control units for a private office building has not been paid. Which legal remedy lets the supplier place a claim against the improved property itself?
- 1032Which type of insurance covers medical costs and lost wages for a fire alarm technician who is injured falling from a ladder on the job?
- 1033A design department manager reviews staffing. Which credential does NFPA 72 list as one way for a fire alarm system designer to show qualification?
- 1034At the end of a new building project, which item is required at the completion of a new fire alarm installation in addition to record drawings and site-specific software?
- 1035When should spot-type smoke detectors normally be installed in a building under construction?
- 1036A building owner asks whether an existing fire alarm system must be upgraded to the newly adopted NFPA 72 edition. Absent other requirements, what is the general rule?
- 1037A service sales manager is preparing an RFP response for the annual testing of a 300 building portfolio. Which item should drive the labor estimate most directly?
- 1038Your company is replacing an obsolete control unit but keeping the existing conventional 2-wire smoke detectors. What must be confirmed before the new unit is ordered?
- 1039When a fire alarm contractor's project manager plans a large project, why is a schedule of values submitted early in the job?
- 1040A project manager is told a key activity on the critical path will finish 5 days late. Which response directly protects the project completion date?
- 1041Which closeout item gives the owner the narrative description of the system, operator instructions and the procedures for routine maintenance and testing?
- 1042A construction manager asks when the fire alarm contractor's warranty period normally starts. What is the most common contract answer?
- 1043At the acceptance test for a new voice evacuation system, the contractor should already have completed which step?
- 1044A cost report shows a job is 50 percent complete, with 62,000 dollars spent against a 110,000 dollar total cost budget. What is the projected cost at completion if the overrun rate continues?
- 1045Which business record should a fire alarm department manager review to compare the estimated and actual labor hours for each completed project?
- 1046A building owner asks why the fire alarm ITM contract must also cover the interface relays for door release and fan shutdown. What is the best explanation?
- 1047When a building has several interconnected fire protection systems and is a high-rise, how often does the IFC require integrated testing in accordance with NFPA 4?
- 1048A department manager wants to cut costs by allowing an uncertified helper to perform the annual testing of a hospital system alone. Which NFPA 72 principle does this conflict with?
- 1049A new owner of a partly renovated building cannot find documentation for the existing system. Which step should a senior technician take first when evaluating it for a repair or replace decision?
- 1050On a large commissioning project, what is the main role of the commissioning authority (CxA)?
- 1051Under NFPA 4, who prepares the integrated system test plan that describes how interconnected fire protection and life safety systems will be tested together?
- 1052In what order do the phases of a typical fire protection commissioning process occur?
- 1053Before the integrated test of a high-rise, what should have been completed for each individual system, such as the fire alarm, sprinkler and smoke control systems?
- 1054What must the record drawings delivered at closeout reflect?
- 1055Your field crew relocated 18 strobes during construction to avoid ductwork. Who is normally responsible for showing these changes on the record drawings?
- 1056A project manager wants the field changes captured accurately for record drawings. Which practice works best?
- 1057Which of these items is normally part of the fire alarm closeout package delivered to the owner?
- 1058At substantial completion of a fire alarm project, what condition normally applies?
- 1059The specification requires owner training on the new voice evacuation system. What should the project manager deliver to show compliance?
- 1060A specification asks the contractor to turn over spare devices equal to 2 percent of each installed device type. What is this deliverable usually called?
- 1061How often must speakers and other audible notification appliances be functionally tested in an ITM program?
- 1062A smoke detector is located above a production line that can only be shut down safely during a planned plant outage. How does NFPA 72 treat testing of devices in such inaccessible areas?
- 1063An owner with a large campus wants to change some test frequencies based on documented device reliability. What does NFPA 72 allow?
- 1064A generator that complies with NFPA 110 is installed as the secondary supply for a fire alarm system. What battery capacity is still required at the control unit?
- 1065A senior PM includes 8 percent contingency in a project budget. What is the purpose of that line?
- 1066Your network shows two technicians needed in week 6 and seven in week 7 for the same project. What scheduling technique smooths these peaks within available float?
- 1067Which item should a fire alarm project manager order immediately after contract award because its lead time often controls the schedule?
- 1068Before installing devices, why must the shop drawings for a new system normally be approved?
- 1069A fire alarm system must recall elevators, close smoke dampers, release doors and shut down air handlers. Which coordination tool should be agreed with the mechanical, elevator and door hardware trades early in the project?
- 1070A company is invited to bid a design build fire alarm upgrade. What is the most important step before preparing the price?
- 1071In a proposal for a retrofit, why should the contractor list clarifications and exclusions?
- 1072Which federal law requires contractors on federally funded construction contracts over 2,000 dollars to pay locally prevailing wages?
- 1073Which federal law requires performance and payment bonds on federal construction contracts above the set threshold?
- 1074How long must an employer keep the OSHA Form 300 injury and illness log?
- 1075During which period must the OSHA Form 300A annual summary be posted in the workplace?
- 1076A technician is hospitalized as an inpatient after a fall on a job site. Within what time must the employer report this to OSHA?
- 1077A former employee left the company 18 months ago after working there for 4 years. Until when must the company keep that person's Form I-9?
- 1078A service van costs 52,000 dollars, has an estimated salvage value of 7,000 dollars and a 5 year useful life. What is the annual straight line depreciation?
- 1079A fire alarm company has 640,000 dollars in current assets and 400,000 dollars in current liabilities. What is its current ratio?
- 1080Using the same figures, 640,000 dollars of current assets and 400,000 dollars of current liabilities, what is the company's working capital?
- 1081A technician earns 34 dollars per hour. Payroll taxes, insurance and benefits add a labor burden of 40 percent. What is the burdened labor cost per hour?
- 1082The burdened labor cost is 47.60 dollars per hour, and the company wants a 32 percent gross margin on service labor. What hourly billing rate meets that target?
- 1083A multi year retrofit contract will buy most devices more than a year after bid. Which contract provision protects the contractor from large material price increases?
- 1084A department manager reports a backlog of 2.4 million dollars. What does backlog mean?
- 1085A fire alarm system is returned to service after a 2 day impairment for a control unit repair. What should happen before the impairment is closed out?
- 1086A failed smoke detector is replaced with an identical model at the same address. What test is required?
- 1087At the end of a project, what is the usual purpose of the AHJ's acceptance test?
- 1088Which role is most important for a Level IV technician acting as liaison on a multi stakeholder project?
- 1089A building owner wants proof each year that the fire alarm ITM program is being followed. Which deliverable best provides this?
- 1090When an operations manager plans staff for a campus ITM contract, why should deficiency repairs be estimated separately from routine testing?
- 1091Which factor makes a cost plus contract riskier for the owner than a lump sum contract?
- 1092A project's planned labor for rough in was 900 hours for 60 percent of the work. Actual hours spent are 1,080 for that 60 percent. What is the labor productivity factor compared with plan?
- 1093Which IBC requirement typically applies before fire alarm work begins in a new building?
- 1094A new service manager wants to measure how well the department keeps customers' systems compliant. Which indicator is most directly related?
- 1095A designer is asked to estimate total amplifier wattage for budgeting a voice system with 220 speakers tapped at 1 watt and 40 speakers tapped at 2 watts. The spec requires 25 percent spare capacity. What minimum amplifier capacity should be budgeted?
- 1096A project manager compares a bid from a subcontractor that is 30 percent below the other bids. What is the most prudent response?
- 1097Which statement about the relationship between the fire alarm contractor and the engineer of record is typically true on a design bid build project?
- 1098A project includes work in an occupied hospital. Which item should be part of the project plan before work begins?
- 1099A company plans its first ERCES installation. Before bidding, which department level decision is most important?
- 1100Which scheduling format shows each activity as a horizontal bar against a calendar, but does not clearly show the logic links between activities?