When a building has several interconnected fire protection systems and is a high-rise, how often does the IFC require integrated testing in accordance with NFPA 4?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1047
- D: At intervals not exceeding 10 years, plus at acceptance and after changes
Explanation
The IFC requires integrated testing per NFPA 4 for high-rise buildings and buildings with smoke control systems at acceptance and at intervals not exceeding 10 years, unless the design or the code official requires a shorter interval. Changes to interconnected systems also call for retesting.
More questions: Installation, Planning and Maintenance Management
- 1048A department manager wants to cut costs by allowing an uncertified helper to perform the annual testing of a hospital system alone. Which NFPA 72 principle does this conflict with?
- 1049A new owner of a partly renovated building cannot find documentation for the existing system. Which step should a senior technician take first when evaluating it for a repair or replace decision?
- 1050On a large commissioning project, what is the main role of the commissioning authority (CxA)?
- 1051Under NFPA 4, who prepares the integrated system test plan that describes how interconnected fire protection and life safety systems will be tested together?
- 1052In what order do the phases of a typical fire protection commissioning process occur?
- 1053Before the integrated test of a high-rise, what should have been completed for each individual system, such as the fire alarm, sprinkler and smoke control systems?