Question 1047 of 243 · NICET Fire Alarm Systems Level IV

When a building has several interconnected fire protection systems and is a high-rise, how often does the IFC require integrated testing in accordance with NFPA 4?

Exactly one answer is correct.

Show solution

Correct answer to question 1047

  • D: At intervals not exceeding 10 years, plus at acceptance and after changes

Explanation

The IFC requires integrated testing per NFPA 4 for high-rise buildings and buildings with smoke control systems at acceptance and at intervals not exceeding 10 years, unless the design or the code official requires a shorter interval. Changes to interconnected systems also call for retesting.