Question 2011 of 243 · NICET Fire Alarm Systems Level IV
A NAC must carry 2.5 A to the end of a 400 ft run, and the voltage may drop no more than 4.4 V. Using solid copper resistances of 3.07 ohms (14 AWG), 1.93 ohms (12 AWG) and 1.21 ohms (10 AWG) per 1,000 ft, what is the smallest conductor that works?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2011
- D: 12 AWG
Explanation
Maximum loop resistance is 4.4 divided by 2.5, or 1.76 ohms. Over 800 ft of loop that allows 2.2 ohms per 1,000 ft. 14 AWG at 3.07 is too high, and 12 AWG at 1.93 meets the limit, so 12 AWG is the smallest size that works.