Question 2012 of 243 · NICET Fire Alarm Systems Level IV

A shop drawing shows a single wall mounted strobe in a 40 ft by 40 ft conference room. What is the minimum effective intensity for that appliance based on the NFPA 72 room spacing table?

Exactly one answer is correct.

Show solution

Correct answer to question 2012

  • A: 60 cd

Explanation

For one wall mounted appliance, the room spacing table requires 60 cd for a 40 by 40 ft room. A 15 cd strobe covers only a 20 by 20 ft room, and 110 cd is the value for about 54 by 54 ft.