Question 2012 of 243 · NICET Fire Alarm Systems Level IV
A shop drawing shows a single wall mounted strobe in a 40 ft by 40 ft conference room. What is the minimum effective intensity for that appliance based on the NFPA 72 room spacing table?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2012
- A: 60 cd
Explanation
For one wall mounted appliance, the room spacing table requires 60 cd for a 40 by 40 ft room. A 15 cd strobe covers only a 20 by 20 ft room, and 110 cd is the value for about 54 by 54 ft.
More questions: Submittals, Shop Drawings and Records
- 2013Where must the system record documents be stored?
- 2014The documentation cabinet for a high-rise is placed in the engineering office instead of at the fire command center. What must be provided at the control unit?
- 2016How long must the record of completion and the record drawings be retained?
- 2017How long must records of a periodic inspection and test be kept under NFPA 72?
- 2018Which statement about the form of NFPA 72 records is correct?
- 2019Where must a copy of the site-specific software be kept after installation or a program change?