Question 4007 of 243 · NICET Fire Alarm Systems Level IV
Where should smoke detectors be placed relative to supply air diffusers?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4007
- C: At least 3 ft away and out of the direct airflow
Explanation
Air from a diffuser can blow smoke away from a detector or dilute it. Detectors are kept out of direct airflow and at least 36 in. from supply diffusers and return openings.
More questions: Complex Detection, Integrated and Special Systems