For spacing purposes, how is each sampling port of an air sampling detection system treated?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4002
- C: As a spot-type smoke detector
Explanation
Each sampling port is treated as a spot-type smoke detector for location and spacing. This lets the designer apply the normal spacing and placement rules to the pipe network.
More questions: Complex Detection, Integrated and Special Systems
- 4003How should an ASD pipe network design be verified before installation?
- 4004How must ASD sampling pipe be identified in the field?
- 4005An ASD system passes its calculated design but field transport time is 40 percent longer. What is the most likely cause?
- 4006A clean room has 60 air changes per hour. How does high airflow affect smoke detector spacing?
- 4007Where should smoke detectors be placed relative to supply air diffusers?
- 4008Heat detectors have a listed spacing of 50 ft. The smooth ceiling is 19 ft high. What spacing applies after the height reduction factor of 0.64?