How must ASD sampling pipe be identified in the field?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4004
- D: Labeled as smoke detector sampling pipe at changes in direction and at regular intervals
Explanation
Sampling pipe must be labeled so other trades do not cut or alter it. Labels go at changes in direction, branches, both sides of penetrations and at regular intervals, often cited as 20 ft.
More questions: Complex Detection, Integrated and Special Systems
- 4005An ASD system passes its calculated design but field transport time is 40 percent longer. What is the most likely cause?
- 4006A clean room has 60 air changes per hour. How does high airflow affect smoke detector spacing?
- 4007Where should smoke detectors be placed relative to supply air diffusers?
- 4008Heat detectors have a listed spacing of 50 ft. The smooth ceiling is 19 ft high. What spacing applies after the height reduction factor of 0.64?
- 4009Where should smoke detectors be placed on a peaked ceiling?
- 4010An atrium has a 90 ft ceiling and a risk of smoke stratification. Which design approach addresses this?