Heat detectors have a listed spacing of 50 ft. The smooth ceiling is 19 ft high. What spacing applies after the height reduction factor of 0.64?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4008
- B: 32 ft
Explanation
Heat detector spacing is reduced for ceilings above 10 ft, because hot gases cool as they rise. For the 18 to 20 ft range the factor is 0.64, so 50 ft x 0.64 = 32 ft.
More questions: Complex Detection, Integrated and Special Systems