Question 4024 of 243 · NICET Fire Alarm Systems Level IV
A double interlock preaction system is being designed. What two events are needed to fill the piping with water?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4024
- A: Detection activation and loss of air pressure from a sprinkler
Explanation
Double interlock preaction requires both a detection signal and loss of supervisory air pressure, which happens when a sprinkler opens. This protects areas where accidental water discharge would be costly.
More questions: Complex Detection, Integrated and Special Systems
- 4025Why is cross-zoning or counting zones used for clean agent release?
- 4026Before testing a releasing system in an occupied data center, what should the technician do?
- 4027Which statement about manual release stations for a clean agent system is correct?
- 4028Which initiating devices may normally initiate elevator Phase I recall?
- 4029A smoke detector in the elevator machine room activates. What additional signal must the elevator receive?
- 4030An elevator hoistway has sprinklers. Where must heat detectors for shunt trip be located?