Which statement about manual release stations for a clean agent system is correct?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4027
- D: Manual release should cause discharge regardless of an abort switch
Explanation
Abort switches are meant to delay automatic release only. A manual release represents a deliberate decision to discharge, so it should not be overridden by an abort switch.